Powering your house is not difficult but will require some modifications to your power distribution board. You will also need a V2L adaptor that is capable of 32 amps. The MG supplied expensive V2L cable is limited to 10 amps.
See the test done on this site.
V2L Test. 7Kw output....
You will need a 3 way 100 amp main switch for Grid/Off/EV and a 32 amp RCCB (residual current circuit breaker) plus 6mm TPS twin core + earth cable to the main switch from an EV socket on the garage wall and preferably 6mm TC+E flexible cable from there to the V2L adaptor. Voltage drop will also be apparent and this will depend on total cable length. I am assuming single phase grid supply here.
This should all be installed by a licenced electrician.
The 32amp RCCB will trip if there is a continuous current demand greater that 32 amps. The cars output will shut off automatically as well when demand gets to this level.
Based on my normal daily usage from the grid my MG4 battery will power my entire house for 9 days if it was 100% full. The problem lies in demand so I could not run several high demand appliances at once like the electric jug, toaster and induction cooktop at the same time and as I have a vertical freezer and fridge freezer there may not be enough to charge the capacitor required to start the motors if other appliances are running.
All this takes is an understanding of the process and your own management of it.
Things will take longer due to voltage drop but they will still run OK. Nominal voltage is 230v but the grid in NSW normally delivers between 240 & 250 volts. The IEC standard of 230 volts at 50 hertz allows for +10% to -6% of the nominal voltage or 253 volts down to 216 volts. Tests from others have shown the MG4 V2L to be at the lower end at 216 volts.