On the subject of earthing, this article explains that inverter power sources cannot necessarily have a N-E connection without the potential of causing serious damage to the inverter.
This is supported by measurements that I made using a multimeter at the MG V2L via a cheap ebay adapter. No load connected.
L to N: 222Vac
E to N: 26Vac
E to L: 196Vac
This does indeed indicate that the E (PE) connection is not tied to N and not to a mid-way point either.
Good of you to have made and detail those readings, thanks. Can you confirm whether the 'E' in those measurements was the earth connection on the V2L lead or the house earth? Also, it would be interesting to repeat said measurements with a 5600 ohm resistor between L and E as that would trigger a 40mA earth leakage current, triggering a typical 30mA RCD. I suspect there is some induced voltage on the lines, but not enough current to be an issue (but that is only guesswork).
With regard to inverter damage, just for clarity, I was not proposing (in post #20 above) to bond N and E on the V2L connection, but to bond the N output to real earth at the termination of the V2L connection, prior to the RCD and prior to the house's critical loads circuit. Then, within the house's critical load circuit there should be an earth rod providing a protective earth reference. Just effectively creating a TT earthing arrangement. This is needed unless the house already has TT earthing, which occurs mostly in rural location with overhead supply.
I don't see (but open to thoughts) as to how that could be in any way detrimental to the inverter as there is no connection to the car's earth (= chassis) and the car itself is not grounded - unless standing in a deep puddle or covered in snow.
I recently had my consumer unit changed and ran three items in the house from the MG V2L. This was only partially successful because the MG discharge stopped by itself on several occasions. I have tried to recreate this failure since, and could not. The first occasion was during wet weather (drizzle), and the second was when it was dry. The conclusion I have come to is that MG inverter does have internal protection but I can only speculate that it might be some sort of current leakage detection.
Interesting - what where the loads? Were they inductive (e.g. fridge / freezer)? There could be restriction on power factor as well, as mentioned in your link.
What we really need to know from MG is:
- What are the V2L output parameters?
- What internal protections are provided?
- What is the recommended earthing connection (if any) when powering a house appliance which is not double insulated (such as a fridge)?
- Does MG recommend any additional protection at the house, such as an RCBO?
I suspect such info will not be available, given that they don't (it seems) even say what the output power limit is. From what I have read, there is overcurrent protection, determined on the resistor value in the V2L lead.
I doubt that the MG would even recommend powering a house from the V2L output either, due to a) the limited supply current and b) the complexity of earthing and safety. My best guess (and what I would say if I were MG) is that the V2L output is designed for powering temporary devices that are double-insulated for camping type activities and hence no earth requirements are relevant.
Would be good to find out more though and to know if any others have gleaned more info from MG.