Isolation transformer already proposed in post #78.
That post concerned supplying a house from the car via a V2L lead.Isolation transformer already proposed in post #78.
Tim, I think an earth rod should be included if a transformer is used. Here's my reasoning...Staffex does offer a good solution to providing a fully floating supply which can then be used to supply a car charger. In fact, removing any earth might be a better solution than using an earth rod - keep the whole thing floating. The problem is size and cost, as a 3kw isolating transformer is quite large and expensive.
Thanks Tim. You whetted my appetite and I found that Podpoint go into some detail here: Why Pod Point homechargers do not require an earth rod | Pod PointBreakdown isolation voltages on isolation transformers is very high, and even higher on medical devices. It is a risk I would prefer in order to keep an isolated supply which could remain isolated right through the charger.
However, as you say, the risk in any normal set-up is pretty low. A few years ago the regulations for car chargers insisted on an earth rod, but I guess further analysis showed this to be a false remedy.
My Podpoint box is external, but the box is plastic, the car connector and cabling are fully insulated, and the car body is not connected to any external or internal power source. So the risk of shock would require several faults - not impossible but unlikely.
My MG5 halts the V2L discharge if it detects an earth (PE) leakage of just over 1mA, which is 30 times more sensitive a typical RCD. See post #87 here: V2L Earthing - how?hello everybody.
I want to connect my MG4 via a V2L to some electrical equipment. this equipment is not using more as 2,500W but I'm wondering, if I need a powerbreaker and earth leakage circuit breaker between the MG4 and the Electrical equipment in case of short cuircuit
Thanks for your reply.
I use the L to E all the time, for laundry washing. If l ask for too much power, it shuts down, then I have to reset the MG4.I cannot seem to find any clear answer on this. How, if at all, does the V2L system provide an earthing system? There is no actual connection to earth, but does it need one?
I’ve read there is some form of in built RCD but I’ve also read no such thing exists. Is an RCD even needed if it is a totally isolated IT type system where the neutral is not ‘earthed’ and thus touching a live conductor wouldn’t allow current to flow through you to earth?
Anyone in the know who knows how the system works, your views would be appreciated.